SWA Armoured cable for greenhouse What size cleats?

  • 2 Replies
  • 2293 Views
*

8ace

  • Newbie
  • *
  • Location: Pontypool South Wales Uk
  • 7
SWA Armoured cable for greenhouse What size cleats?
« on: November 04, 2012, 14:01 »
I have 16.5mm outside over all diameter of outer sheath SWA cable running into the greenhouse. However the clips seem to be sizes rather than outer dia. I think I need size 7 cleats can anyone confirm this as I can't find any clear info as they all seem to work off the mm2 of copper.

Thanks in advance 8)

*

fatcat1955

  • Hero Member
  • *****
  • Location: Hunsdon Herts
  • 1441
Re: SWA Armoured cable for greenhouse What size cleats?
« Reply #1 on: November 04, 2012, 19:34 »
size 7 is correct. Please ensure that you install a 30ma RCD on this circuit.

*

8ace

  • Newbie
  • *
  • Location: Pontypool South Wales Uk
  • 7
Re: SWA Armoured cable for greenhouse What size cleats?
« Reply #2 on: November 04, 2012, 19:56 »
cool thanks,
there are 2 rcds (split load board I think it was called) on the dist board
cheers
 



xx
greenhouse size query

Started by mushroom on Equipment Shed

31 Replies
11374 Views
Last post January 16, 2008, 11:00
by gobs
xx
Lean to greenhouse help / 6x3 size anywhere?

Started by dougens on Equipment Shed

5 Replies
3160 Views
Last post January 26, 2021, 20:15
by dougens
xx
Flymo cable

Started by Spana on Equipment Shed

7 Replies
5158 Views
Last post July 16, 2009, 08:39
by Spana
xx
Al-ko MH3540-4 Clutch Cable

Started by newtonuk on Equipment Shed

1 Replies
1390 Views
Last post April 24, 2019, 23:00
by jezza
 

Page created in 0.139 seconds with 38 queries.

Powered by SMFPacks Social Login Mod
Powered by SMFPacks SEO Pro Mod |